A simply-supported W21x111 interior beam made of A992 steel supports a single fl
ID: 1839222 • Letter: A
Question
A simply-supported W21x111 interior beam made of A992 steel supports a single floor level with a span length of 50 ft and a tributary width of 25 ft. The compression flange of the beam is braced at each end and at midspan. The beam will be subjected to a uniform dead load (excluding self-weight) of 75 psf and a nominal (unreduced) live load of 50 psf. Serviceability requirements are set at a maximum deflection of L/240 for the combination of dead load and live load, and L/360 under the live load alone.
a). The beam's factored moment capacity
b). The beam's factored shear force capacity
c). The beam's allowable deflections for dead & live load and live load by itself
d). The ultimate moment demand
e). The ultimate shear force demand
f). The maximum deflections for dead & live load and live load by itself.
g). Considering results from parts a).-f). is the W21x111 sufficient to resist this loading?
Explanation / Answer
a) Unbraced length of beam=50/2=25 ft
Per Table 3-2 of AISC, moment capacity of beam for Unbraced length of 25 ft=1050- (1050-654)/(31.2-10.2)*(25-10.2)=771 kip-ft
b)beam's shear force capacity per Table 3-2 =355 kips
c)total allowable deflection=L/240=50*12/240=2.5 inches
Live load deflection limit=L/360=50*12/360=1.67 inches
d)Dead load on beam=75*25=1875 plf
Self weight of beam=111 plf
Total dead load=1875+111=1986 plf=1.986 kip/ft
Total live load=50*25=1250 plf=1.25 kip/ft
Total factored load=(1.2*1.986)+(1.6*1.25)=4.3832kip/ft
Ultimate moment in beam=4.3833*50²/8=1369.75 kip-ft