Academic Integrity: tutoring, explanations, and feedback — we don’t complete graded work or submit on a student’s behalf.

Thanks for having the time to read my question. A 50kVA, 1-phase, 60 Hz, 4400/20

ID: 2991177 • Letter: T

Question

Thanks for having the time to read my question.

A 50kVA, 1-phase, 60 Hz, 4400/200 V distribution transformer has a maximum efficiency at full load. The transformer gave the following test results

Open-circuit test: 4400 V applied to HT side, power taken 320 W.

Short-circuit test: Secondary short-circuited, power taken 320 W at full load.

Calculate the transformer energy efficiency (all-day efficiency) for the load cycle over 24 hour period given that the transformer works at full-load for 4 hours, at half load for 8 hours, at quarter load for 6 hours and at no-load for 6 assuming a unity power factor.

Explanation / Answer

Energy Output = kva*cos?*Kwh

%Rated Load

pf

x* kva cos?

KW

Hours

O/P Kwhs

1   

1

1*1*50

50

4

200

1/2

1

0.5*1*50

25

8

200

1/4

1

.25*1*50

12.5

6

75

0

1

0

0

6

0

Copper loss at load = m*m*copper loss at any load

Copper loss at rated load

%Rated Load

m

KW

Hours

O/P Kwhs

1   

1   

50

4

1.28

1/2

1/2

25

8

1.28

1/4

1/4

12.5

6

0.48

0

0

0

6

3.04Kwh

Total Energy Output over 24 hr period excluding 6 hrs at no load is Wout = 475kwH.

Total Energy loss in the core for 24hrs including 6 hrs at no load ,

OC test = Pi*t = (320/1000)*24= 7.68Kwh.

Given Copper loss at rated load = 320Watts.

All day efficiency = Wout/( Wout+Wi+wC)= 475/485.72 = 97.792 Percent

Energy Output = kva*cos?*Kwh

%Rated Load

pf

x* kva cos?

KW

Hours

O/P Kwhs

1   

1

1*1*50

50

4

200

1/2

1

0.5*1*50

25

8

200

1/4

1

.25*1*50

12.5

6

75

0

1

0

0

6

0