2. Design a one-way floor slab for an industrial building. The slab will be indo
ID: 2311806 • Letter: 2
Question
2. Design a one-way floor slab for an industrial building. The slab will be indoors (not exposed to weather) and will have a simple span of 8'-0". The floor must support a superimposed dead load of 25 psf (in addition to the slab selfweight) and a live load of 150 psf. Use a slab thickness of 5" and use #4 reinforcing (choose most efficient spacing allowed by code). Select temperature and shrinkage steel and check minimum reinforcing requirements. Concrete compressive strength, fe 4000 psi, and the steel is grade 60 Wuve 9-0Explanation / Answer
Solution:-
Design one way slab
Depth = 5 inch
Dead load = 25 psf
Live load = 150 psf
Total load = 175 psf
Factored load = 1.5 * 175 = 262.5 psf
Factored B.M. = wul2/8
Assume steel consist of #4 bars , 0.5 inch diameter bars are used with 0.59 inch clear cover
Effective depth (d) = 5 – 0.59 = 4.41 inch
Effective span of slab = 8 + 4.41/12 = 8.36 feet
Bending moment = 262.5 * 8.362/8
= 2293.25 pound – feet
Area of steel
Mu = 0.87fyAst*( d – fyAst/(fckb))
2293.25 *12 = 0.87* 60000 * Ast*(4.41 – 60000*Ast/(4000*39.36))
Ast = 11.47 inch2
Use #4 bars @ 6 inch spacing
Temperature reinforcement equal to 0.15 % of the gross concrete area will be provided in the longitudinal direction
= 0.0015*39.36*4.41 =0.26 inch2
Use #4 bars @ 5 inch spacing
Minimum area of reinforcement = 0.12% of total cross sectional area
= 0.12/100 * 39.36*5 = 0.23 inch2
So provided reinforcement is safe