A pump station has been designed to lift water out of a 6 metre deep pit (vented
ID: 2993542 • Letter: A
Question
A pump station has been designed to lift water out of a 6 metre deep pit (vented to atmosphere) via a centrifigual pump mounted at ground level.
Liquid conditions 20 OC
Suction pipe work losses 2.0 metres
NPSH safety factor 5.0 kPa
Vapor pressure @ 20oC 0.25 metres
Calculate the Net Positive Suction Head (NPSH) for the system ?
In summer the liquid temperature rises to 60 oC, this changes the water vapor pressure to 2.05 metres. What is the revised NPSH for the higher water temperature ?
Pressure loss in the suction pipe work is directly proportional to water veloicty in the pipe work squared, which is inversely proportional to suction pipe work diameter squared.
Explanation / Answer
P1 + 1/2*p*v1^2 + p*g*z1 = Patm + 1/2*p*v2^2 + p*g*z2 + p*g*Hloss
z1 = 6 m
z2 = 0 m
v2 = 0 m/s
P1/(p*g) +1/2*v1^2/g + z1 = Patm/p*g + 0 +0 + Hloss
h1 + v1^2/(2*g) + 6 = 10^5/(1000*10) + 2
h1 + v1^2/(2*g) = 6
NPSH = h1 + v1^2/(2*g) = 6 m and
(h1 - hvap) > 0 to avoid cavitation
h1>0.25 m
In summer
NPSH = 6 m and
(h1-hvap)>0
h1>2.05 m
Related Questions