Academic Integrity: tutoring, explanations, and feedback — we don’t complete graded work or submit on a student’s behalf.

answer 5? 6? 7? 8? 9? which table of nec 2014 i should use? 2.9m x 24h 5) Write

ID: 2085436 • Letter: A

Question


answer
5?
6?
7?
8?
9?
which table of nec 2014 i should use?

2.9m x 24h 5) Write size of conductor THWN: for total load of 50 amps, if conduit is installed at:4be 30 degrees C (TA ambient temperature) with: (3) current-carrying conductors 6) Write size of conductor THWN: for total load of 50 amps, if conduit is installed at: (30 degrees C (TA-ambient temperature) with: (7) current-carrying conductors 1 write size of conductor THWN: for total load of 50 amps, if conduit is installed at: 40 degrees C (TA= ambient temperature) with: (3) current carrying conductors 7 dec 8) Determine bending radius allowed for conductor: AWG 600kcmil THWN 9) Specify size for equipnunt grounding conductor, if circuit is protected with 300A breaker

Explanation / Answer

8).The bending radius allowed for conductor AWG 600 kcmil THWN Eight times the overall cable diameter

9)The size of equipment is 4AWG CU.