50. Calculate the sanitary flow for a 6,000 sf non-medical office building with
ID: 1866668 • Letter: 5
Question
50. Calculate the sanitary flow for a 6,000 sf non-medical office building with Daily flow____________________________________________________________ Minimum Required Size of Septic Tank ____________________________________ Required leaching pools______________________________( specify number and dimensions ) Future Expansion vertical feet of 8' Diameter leaching pools . _________________( specify number and dimensions)
Notes: Flow rate for non-medical office building is 0.06 gpd/sf Leaching rate is 1.5 gal/sq. ft./day . 8' diameter tank = 25.12 sf leaching area per vertical foot
Explanation / Answer
Assuming 90% of water supplied change to sanitary flow
Water supplied = 0.06 gpd/sf
Area of building = 6000 sf
Thus total water supplied = 0.06*6000= 360 gpd
Thus total sanitary flow = 0.9* 360 = 324 gallons per day
As per thumb rule for 0-500 gpd of sanitary flow effective size of septic tank is 900 gallons but in most US jurisdictions the minimum septic tank size is 1000 gallons thus minimum required size of septic tank would be 1000 gallons
As a thumb rule Leaching tank size required = 0.45*1000 = 450 gallons
Surface area = 450/1.5 = 300 sf
Now maximum width =2' let length = 10'
Thus number of leaching pools = 300/20= 15