A 400kV, 60Hz overhead line has the following parameters: Rated Power 600MVA Len
ID: 1801878 • Letter: A
Question
A 400kV, 60Hz overhead line has the following parameters: Rated Power 600MVA Length 200km Resistance at 20degreeC 0.03329Ohm/km at 60Hz Inductance 1.035mH/km Temperature co-efficient of Resistance = 0.00403K-1 If the line is carrying its rated current, the sending end is at rated voltage and the line temperature is 70degreeC, calculate the voltage drop in the line? Note that RT = R20degree(1 + alpha (T - 20degreeC)) What capacitor should be inserted in series with each phase of the line to reduce the magnitude of the voltage drop in the line to 10% of rated voltage at rated current?Explanation / Answer
PART A
as P=IV
P=600MVA
V=400KV
SO I=P/V=1500A
BY USING ABOVE GIVEN FORMULA
R70=.0399ohm
SO V=IR =1500*.0399=59.85V
PART B
AS 10% OF RATED VOLTAGE IS 40KV SO
IMPEDENCE WIL
X=40000/1500
X=26.667
X=1/2FC
SO C=9.95*10-5 F
C100F